Steve Anderson wrote:Harry, you do need to disconnect all loads to see if you have saturating cores. A perfectly normal transformer winding with a bridge rectifier, capacitor and regulator looks like below. this is due to the diodes, capacitors and in-built transformer losses. With no load at all it's a sine-wave, that's why I said no load.
The flat part is where most of power is lost in the transformer and why they get hot, but within design ratings. With saturating cores the same general shape applies but the 'shoulders' will be more rounded, not so square...again with no load.
The best way to check this is with a scope, look at the 330/340V waveform with no load, it should be a nice 50Hz sine. If the peaks and troughs are 'crushed' then the cores are saturating - not good.
Steve A.
Steve due to the ac voltage is 300 volt its way out of range on my scope all i can see is the middle of the waveform .mmmm head scratching time ..could use another transformer and drop it back to something i can read ...but not right i bet ..